VISION In-Wall Dual Relay Switch ZL7432 status update problem

Posted: 06 Jul 2018 06:54
by joluzu
both relays works from the interface.
but only sw1 update the GUI after a manual change.( sw2 don't update the GUI).
in the device manual I found the reason :

"For Wall SW1, ZL 7432 will report the status of On/OFF after doing “Association”.
However, Wall SW2 will only report the status if Z-Wave™ Interface Controller
support Multi Channel command, and send Get Command to ask ZL 7432 Wall SW
2 to report the status."

but I don't know how can achieve this.

thank you in advanced for your help

Re: VISION In-Wall Dual Relay Switch ZL7432 status update problem

Posted: 11 Jul 2018 07:50
by joluzu
is somebody is interested I found the workaround:

basically when s2 is switched manually. the device send the status of the s1 to the controller. at that point you must update s2 getting the status update